Friends:



It was only recently that I started working on Sunny Island systems. I have
inherited two systems from installers that have flaked out and/or could not
resolve problems. Both systems are operating unreliably for a number of
reasons.



Both systems suffered from chronic generator starting issues. We have been
able to separate out those issues and what remains is some serious questions
about the inherent reliability of these inverters.



What is equally troubling is the response I have received from SMA tech
support. It started with being questioned on the quality of my workmanship
without any evidence to support the claims. SMA does not provide any BOS
components so in addition to it being difficult to integrate these systems,
tech support has no experience with bypass options and DC OCPD components
manufactured by others.



We have experienced unexplained outages, some with cryptic error codes, some
without any error indications, just AC output voltage disappearing or going
very low (60 to 80 volts).



It is my impression that SMA tech support is now guessing at what is going
on. I have been told to "check connections" and wiggle things in order to
diagnose an anti-islanding error in an off-grid installation. I have also
been told that a generator shut down that occurred 6.5 minutes prior to the
problem caused the ant-islanding problem. I receive responses that just
don't appear to be well thought out. Anyone else experience any of these
problems?



We have also been told that the transfer relay is prone to "sticking" and we
have to power the units down and "tap" on the relays.



Have any of you experienced similar inexplicable problems?



I have gained some expertise in analyzing the card data. One can easily
open event and failure files. The log files are trickier. There is a new
record created every minute with about 130 fields. You can import them into
a spreadsheet and browse around for trends and deviations from the norm. I
am writing macros to reveal and hide columns as needed and to generator
graphs.



Below is a list of some of the error codes we have experienced that no one
will explain to us. I am hoping someone can tell me what they mean and what
may cause them. Both systems are off-grid with Sunny Boy mini-grid systems
and generators.





E110 Error Shutdown Shutting down due to error (Probably due to error
described in prior code)



F117 AC Current Limit (short circuit control active for too long)



E118 Autostart (I guess tries to start but can't due to persistent error)



F141 Inverter Voltage Low (why?)



W159 Voltage on Output AC1 Slave (we were told this is the sticky transfer
relay)



W315 External Voltage Low



W331 Grid/generator disconnected due to anti-islanding



W351 Disconnected from external source due to extended short circuit (short
circuit in what? How long? Corrective action?)



F710 Autostart meter elapses



W738 Gen Sync Loss



Thanks,



William Miller









Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140825/037bf154/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <Loading Image...>
Matt Partymiller
2014-08-25 19:19:22 UTC
Permalink
William,

In general I have found the SI to be more reliable than other similar
products. My one grievance is the 'tap' error you mention. We have units
from more than 5 years ago where this method of failure is the norm in
grid-tie battery backup mode. Basically, the power goes out, the SI relay
fails and the house is in the dark. SMA should really recall those
products.

My contact at SMA for their SI can be reached at 916-316-7170. He may be
far more helpful.

Matt
Post by William Miller
It was only recently that I started working on Sunny Island systems. I
have inherited two systems from installers that have flaked out and/or
could not resolve problems. Both systems are operating unreliably for a
number of reasons.
Both systems suffered from chronic generator starting issues. We have
been able to separate out those issues and what remains is some serious
questions about the inherent reliability of these inverters.
What is equally troubling is the response I have received from SMA tech
support. It started with being questioned on the quality of my
workmanship without any evidence to support the claims. SMA does not
provide any BOS components so in addition to it being difficult to
integrate these systems, tech support has no experience with bypass
options and DC OCPD components manufactured by others.
We have experienced unexplained outages, some with cryptic error codes,
some without any error indications, just AC output voltage disappearing or
going very low (60 to 80 volts).
It is my impression that SMA tech support is now guessing at what is
going on. I have been told to "check connections" and wiggle things in
order to diagnose an anti-islanding error in an off-grid installation. I
have also been told that a generator shut down that occurred 6.5 minutes
prior to the problem caused the ant-islanding problem. I receive
responses that just don't appear to be well thought out. Anyone else
experience any of these problems?
We have also been told that the transfer relay is prone to "sticking" and
we have to power the units down and "tap" on the relays.
Have any of you experienced similar inexplicable problems?
I have gained some expertise in analyzing the card data. One can easily
open event and failure files. The log files are trickier. There is a new
record created every minute with about 130 fields. You can import them
into a spreadsheet and browse around for trends and deviations from the
norm. I am writing macros to reveal and hide columns as needed and to
generator graphs.
Below is a list of some of the error codes we have experienced that no
one will explain to us. I am hoping someone can tell me what they mean
and what may cause them. Both systems are off-grid with Sunny Boy
mini-grid systems and generators.
E110 Error Shutdown Shutting down due to error (Probably due to error
described in prior code)
F117 AC Current Limit (short circuit control active for too long)
E118 Autostart (I guess tries to start but can't due to persistent error)
F141 Inverter Voltage Low (why?)
W159 Voltage on Output AC1 Slave (we were told this is the sticky
transfer relay)
W315 External Voltage Low
W331 Grid/generator disconnected due to anti-islanding
W351 Disconnected from external source due to extended short circuit (short
circuit in what? How long? Corrective action?)
F710 Autostart meter elapses
W738 Gen Sync Loss
Thanks,
William Miller
Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/> 805-438-5600
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
http://www.mail-archive.com/re-wrenches at lists.re-wrenches.org/maillist.ht
ml
www.re-wrenches.org/etiquette.htm
www.members.re-wrenches.org
Matthew Partymiller
Solar Energy Solutions LLC
(877) 312-7456
matt at solar-energy-solutions.com

Loading...