Dear Wrenches,

Several of your co-wrenches are helping Mike Holt with the video
companion to his PV & the NEC 2014 book. So since you spend all your
weekdays thinking about the NEC, what better way to spend this weekend
than to watch NEC nerds discuss the meanings of shalls and shall-nots,
the unwelcome return of 690.47(D), and the continued flights of our
favorite sections to 705, right? Before you answer that, know that you
can also ask questions during the video in case something is unclear or
if we're wrong about something.

Broadcasting (free) from:
www.MikeHolt.com/live

Times:
~9a-4p ET Sat 12/7
~9a-5p ET Sun 12/8

Video from this weekend will be what's edited into the official DVD that
Mike puts out in the next few weeks.

Because Bill Brooks has a great joke about separate direct-current
grounding electrode systems bonded to the alternating current grounding
electrode systems that you don't want to miss,
Dave

PS If this post violates list etiquette, my apologies in advance,
Michael. We don't get a commission, if that helps...
Richard L Ratico
2013-12-09 14:21:35 UTC
Permalink
An embedded and charset-unspecified text was scrubbed...
Name: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/f9aa00df/attachment.txt>
Doug Wells
2013-12-09 16:30:48 UTC
Permalink
Richard,

I agree. I caught part of the streaming as well.
Thanks for sharing.
Bringing lightning protection into the discussion is a whole other can of worms.
He made a variety of assumptions.
1. That the auxiliary rods were not bonded. For instance, I was trained in the exact opposite manner for ground mounts and off grid. Installing a rod at each pole mount, inverter and generator. But then bonding all of these rods together, with the intention of keeping all metal, modules, etc in the entire system at the same potential. This approach seems to really be echoing his own comments of keeping everything underground bonded. The important part seems to be having the DC electrical bonding, GFI etc and the AC neutral bond in only one location.
2. Ground lightning strikes will create differences in potential on all conductors. The insulation on most conductors buried in conduit is only good to 600 to 1000 volts at best. If there is a strike creating 100,000's of volts then all conductors will surely see current and voltage spikes. This is why we always install Surge Arrestors.
3. While I can appreciate the physics of lightning protection, I have it on my house, I am not so sure about its impact on a large PV array. I have a hard time accepting that a 1-2 foot spike of metal on the roof connected directly to ground will handle anything near a direct strike like he showed in the picture. Unfortunately, in that regard you get hit, or you don't. In fact, some lightning folks will admit that lightning protection can encourage the passage of some strikes. But the question here seems to be ---1. Is 1000 ft2 of aluminum rectangles, racking and wire, less conductive than a 2 foot metal spike. And is the extra 20-100 feet that the grounds pass to the rod, really enough to resist current in a strike. 2. If logic holds that a lightning protection system has merit, then wouldn't bringing every rail to ground at multiple points and then bonding them all together do the same thing.
I am not saying that this is the way it should be done, but making the point that it is essentially the same thing.
So, I respect Mike and what he is trying to do for many people, which is provide clear and accurate training materials.
However, I agree with Richard that I would like to hear from all the voices in the industry that have their minds around this as well.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

On Dec 9, 2013, at 9:21 AM, Richard L Ratico wrote:

I watched most of the streaming video of Mike Holt and six PV industry
professionals this weekend. The most interesting aspect of it was Mr. Holt's
very dramatic build up to the Sunday discussion of Article 690.47(D) which
brings back the requirement for an auxiliary grounding electrode for PV arrays.
He used everything short of drum rolls to build anticipation for this part of
the presentation.

Having personally contributed a short piece on this subject for SolarPro
magazine along with Bill Brooks and John Wiles in 2008, I looked forward to this
discussion. Finally, midday Sunday, instead of a discussion of an important and
controversial part of the 2014 code, we received a rant by Mr. Holt demanding an
immediate and unprecedented withdrawal of the article.

Prior to his remarks, in contrast to the preceding article discussions, Mr. Holt
asked that the guest panel not make any comments that would explain how the
requirement came to return to the code after being eliminated in the 2011
edition, or any comment that might "confuse" the issue. To my very great
surprise and disappointment, they complied, uttering not a single word, nodding
their heads and moving on to the next article.

After all the buildup by Mr. Holt, the "discussion" amounted to his monolog,
which if parsed, though stated to be for safety concerns, seemed primarily an
exercise designed to sell his books, videos and consulting services on
grounding. This was of course expected. The weekend live streaming was
generously offered free of charge, a rare opportunity to hear current PV expert
opinion on the NEC. My concern is that Mr. Holt's control of the process here
inhibited the dialog that should have taken place.

There are significant implications of allowing his opinion to go unchallenged.
Is there, or is there not, any merit in 690.47(D)? Could the language be better?
Could the requirement be modified to make it better rather than simply
discarding it? Does accepting his argument mean all those systems installed
according to the 2008 code are unsafe?

Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better to
carefully think through and discuss the issue, in contrast to what was permitted
on his "show"?

Dick Ratico
Solarwind Electric


--- You wrote:
Dear Wrenches,

Several of your co-wrenches are helping Mike Holt with the video
companion to his PV & the NEC 2014 book. So since you spend all your
weekdays thinking about the NEC, what better way to spend this weekend
than to watch NEC nerds discuss the meanings of shalls and shall-nots,
the unwelcome return of 690.47(D), and the continued flights of our
favorite sections to 705, right? Before you answer that, know that you
can also ask questions during the video in case something is unclear or
if we're wrong about something.

Broadcasting (free) from:
www.MikeHolt.com/live

Times:
~9a-4p ET Sat 12/7
~9a-5p ET Sun 12/8

Video from this weekend will be what's edited into the official DVD that
Mike puts out in the next few weeks.

Because Bill Brooks has a great joke about separate direct-current
grounding electrode systems bonded to the alternating current grounding
electrode systems that you don't want to miss,
Dave

PS If this post violates list etiquette, my apologies in advance,
Michael. We don't get a commission, if that helps...
_______________________________________
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
Jason Szumlanski
2013-12-09 19:21:40 UTC
Permalink
I had to quit watching at noon, so I was disappointed to have missed the
theatrics. I just installed a system on my home to NEC 2008 as is followed
here. I have convinced a local plans reviewer that since it was removed in
NEC 2011, the building official should waive the 690.47(D) requirement for
rooftop systems. He specifically asked me if it would return in NEC 2014,
and if I am reading this right, the answer is definitely "no."

Since there was no aesthetically acceptable way to run the additional GEC
in my case and make it "as close as practicable (which is ambiguous
anyway), I cut it out immediately following inspection - something I would
NEVER recommend a customer do, of course. Nonetheless, I feel this was a
reasonable and acceptable move given that there are thousands of systems
out there inspected under NEC 2011 that have not additional grounding
electrode.

I will continue to listen with great interest...

Jason Szumlanski

Fafco Solar





On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico <
Post by Doug Wells
Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to
carefully think through and discuss the issue, in contrast to what was
permitted
on his "show"?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/8a384d4d/attachment.htm>
Brian Mehalic
2013-12-09 19:30:23 UTC
Permalink
Here's a link to the video:



Brian
I had to quit watching at noon, so I was disappointed to have missed the theatrics. I just installed a system on my home to NEC 2008 as is followed here. I have convinced a local plans reviewer that since it was removed in NEC 2011, the building official should waive the 690.47(D) requirement for rooftop systems. He specifically asked me if it would return in NEC 2014, and if I am reading this right, the answer is definitely "no."
Since there was no aesthetically acceptable way to run the additional GEC in my case and make it "as close as practicable (which is ambiguous anyway), I cut it out immediately following inspection - something I would NEVER recommend a customer do, of course. Nonetheless, I feel this was a reasonable and acceptable move given that there are thousands of systems out there inspected under NEC 2011 that have not additional grounding electrode.
I will continue to listen with great interest...
Jason Szumlanski
Fafco Solar
Post by Doug Wells
Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better to
carefully think through and discuss the issue, in contrast to what was permitted
on his "show"?
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
www.re-wrenches.org/etiquette.htm
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/dd59fbf8/attachment.htm>
Brian Mehalic
2013-12-09 20:03:49 UTC
Permalink
And it's definitely back in 2014.

Typos courtesy of my iPhone.
I had to quit watching at noon, so I was disappointed to have missed the theatrics. I just installed a system on my home to NEC 2008 as is followed here. I have convinced a local plans reviewer that since it was removed in NEC 2011, the building official should waive the 690.47(D) requirement for rooftop systems. He specifically asked me if it would return in NEC 2014, and if I am reading this right, the answer is definitely "no."
Since there was no aesthetically acceptable way to run the additional GEC in my case and make it "as close as practicable (which is ambiguous anyway), I cut it out immediately following inspection - something I would NEVER recommend a customer do, of course. Nonetheless, I feel this was a reasonable and acceptable move given that there are thousands of systems out there inspected under NEC 2011 that have not additional grounding electrode.
I will continue to listen with great interest...
Jason Szumlanski
Fafco Solar
Post by Doug Wells
Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better to
carefully think through and discuss the issue, in contrast to what was permitted
on his "show"?
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
www.re-wrenches.org/etiquette.htm
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/a43c6854/attachment.htm>
Glenn Burt
2013-12-09 20:50:50 UTC
Permalink
The bad news from the 2014 codebook:



690.47 Grounding Electrode System.

(D) Additional Auxiliary Electrodes for Array Grounding.

A grounding electrode shall be installed in accordance

with 250.52 and 250.54 at the location of all ground- and

pole-mounted PV arrays and as close as practicable to the

location of roof-mounted PV arrays. The electrodes shall be

connected directly to the array frame(s) or structure. The dc

grounding electrode conductor shall be sized according to

250.166. Additional electrodes are not permitted to be used

as a substitute for equipment bonding or equipment grounding

conductor requirements. The structure of a ground- or

pole-mounted PV array shall be permitted to be considered

a grounding electrode if it meets the requirements of

250.52. Roof-mounted PV arrays shall be permitted to use

the metal frame of a building or structure if the requirements

of 250.52(A)(2) are met.

Exception No. 1: An array grounding electrode(s) shall

not be required where the load served by the array is integral

with the array.

Exception No. 2: An additional array grounding electrode(

s) shall not be required if located within 1.8 m (6 ft)

of the premises wiring electrode.





-Glenn



From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Monday, December 09, 2013 2:22 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only



I had to quit watching at noon, so I was disappointed to have missed the
theatrics. I just installed a system on my home to NEC 2008 as is followed
here. I have convinced a local plans reviewer that since it was removed in
NEC 2011, the building official should waive the 690.47(D) requirement for
rooftop systems. He specifically asked me if it would return in NEC 2014,
and if I am reading this right, the answer is definitely "no."



Since there was no aesthetically acceptable way to run the additional GEC in
my case and make it "as close as practicable (which is ambiguous anyway), I
cut it out immediately following inspection - something I would NEVER
recommend a customer do, of course. Nonetheless, I feel this was a
reasonable and acceptable move given that there are thousands of systems out
there inspected under NEC 2011 that have not additional grounding electrode.



I will continue to listen with great interest...



Jason Szumlanski

Fafco Solar





<Loading Image...
&u=ce9344a8140ce271>



On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico
<Richard.L.Ratico at valley.net> wrote:


Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to
carefully think through and discuss the issue, in contrast to what was
permitted
on his "show"?





-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/465a75ba/attachment.htm>
Brian Mehalic
2013-12-09 21:21:26 UTC
Permalink
I agree with Mike on this, as written this is a bad Section, and in reality
there is no need for it, so deleting it is better than trying to fix
something that is unnecessary.

The 2014 690.7(D) language has changed - the title is now "Additional
Auxiliary Electrodes.."; in 2008 the title to be "Additional
Electrodes...". It can be confusing to keep the terminology straight, but:


- "Additional Electrodes" from 2008 is seemingly undefined,
- "Supplemental Electrodes" may be required as part of the grounding
electrode system per 250.53(A)(2) and (3)
- Auxiliary electrodes are defined in 250.54


It's the allowances for Auxiliary Electrodes which cause the problem.
250.54, which must be followed per 690.47(D), states that auxiliary
electrodes do not have to be bonded to the grounded electrode system (as is
typically required of all present electrodes per 250.50), nor does it have
to follow the bonding jumper sizing requirements of 250.53(C).

This creates the problem Mike describes - two connections to ground that
can have dramatically different potential between them in the event of a
lightning incident.

I've always been a proponent of bonding residential pole and ground-mounted
PV structures back to the grounding system of the building they serve.
Large ground-mounted solar farms have lot of
auxiliary/supplemental/additional electrodes in the form of pilings, and
the systems I work on have these all bonded together and back to the
electrodes at the inverter pads - it's extra copper in the ground but it
helps alleviate the problem of different potentials.

The problem is for roof-mounted systems; the 2008 language, by not
explicitly calling it an auxiliary electrode, basically meant that
inspectors were requiring the additional electrode to be bonded to the
existing grounding electrode system on the building - which alleviates the
concerns of having two connections to the Earth. Now 2014 calls it
"Auxiliary" and the language in 250 specifically says it doesn't have to be
bonded to the grounding electrode system - enter the safety concerns
described by Mike and Bill.

Not having to bond the 690.47(D) Auxiliary electrode to the grounding
electrode system alleviates some of the pain of having to put that rod in,
so I imagine that many installers will take this route if the AHJ allows
it. Thus the need to do something about this, before it lingers for years
and years. So...go Bill!





Brian Mehalic
NABCEP Certified Solar PV Installation Professional? R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org
*690.47 Grounding Electrode System.*
*(D) Additional Auxiliary Electrodes for Array Grounding.*
A grounding electrode shall be installed in accordance
with 250.52 and 250.54 at the location of all ground- and
pole-mounted PV arrays and as close as practicable to the
location of roof-mounted PV arrays. The electrodes shall be
connected directly to the array frame(s) or structure. The dc
grounding electrode conductor shall be sized according to
250.166. Additional electrodes are not permitted to be used
as a substitute for equipment bonding or equipment grounding
conductor requirements. The structure of a ground- or
pole-mounted PV array shall be permitted to be considered
a grounding electrode if it meets the requirements of
250.52. Roof-mounted PV arrays shall be permitted to use
the metal frame of a building or structure if the requirements
of 250.52(A)(2) are met.
*Exception No. 1: An array grounding electrode(s) shall*
*not be required where the load served by the array is integral*
*with the array.*
*Exception No. 2: An additional array grounding electrode(*
*s) shall not be required if located within 1.8 m (6 ft)*
*of the premises wiring electrode.*
-Glenn
re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Jason Szumlanski
*Sent:* Monday, December 09, 2013 2:22 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only
I had to quit watching at noon, so I was disappointed to have missed the
theatrics. I just installed a system on my home to NEC 2008 as is followed
here. I have convinced a local plans reviewer that since it was removed in
NEC 2011, the building official should waive the 690.47(D) requirement for
rooftop systems. He specifically asked me if it would return in NEC 2014,
and if I am reading this right, the answer is definitely "no."
Since there was no aesthetically acceptable way to run the additional GEC
in my case and make it "as close as practicable (which is ambiguous
anyway), I cut it out immediately following inspection - something I would
NEVER recommend a customer do, of course. Nonetheless, I feel this was a
reasonable and acceptable move given that there are thousands of systems
out there inspected under NEC 2011 that have not additional grounding
electrode.
I will continue to listen with great interest...
Jason Szumlanski
Fafco Solar
On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico <
Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to
carefully think through and discuss the issue, in contrast to what was
permitted
on his "show"?
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
www.re-wrenches.org/etiquette.htm
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/d298697b/attachment.htm>
August Goers
2013-12-09 21:47:58 UTC
Permalink
Hi Glenn,



This is a confusing passage without seeing the context from the other parts
of 690.47 (A, B, C etc). Can you send the full passage if it?s handy for
you? My 2014 NEC is in the mail so I have yet to see the full implications
of this section.



Best,



August



*From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Glenn Burt
*Sent:* Monday, December 09, 2013 12:51 PM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only



The bad news from the 2014 codebook:



*690.47 Grounding Electrode System.*

*(D) Additional Auxiliary Electrodes for Array Grounding.*

A grounding electrode shall be installed in accordance

with 250.52 and 250.54 at the location of all ground- and

pole-mounted PV arrays and as close as practicable to the

location of roof-mounted PV arrays. The electrodes shall be

connected directly to the array frame(s) or structure. The dc

grounding electrode conductor shall be sized according to

250.166. Additional electrodes are not permitted to be used

as a substitute for equipment bonding or equipment grounding

conductor requirements. The structure of a ground- or

pole-mounted PV array shall be permitted to be considered

a grounding electrode if it meets the requirements of

250.52. Roof-mounted PV arrays shall be permitted to use

the metal frame of a building or structure if the requirements

of 250.52(A)(2) are met.

*Exception No. 1: An array grounding electrode(s) shall*

*not be required where the load served by the array is integral*

*with the array.*

*Exception No. 2: An additional array grounding electrode(*

*s) shall not be required if located within 1.8 m (6 ft)*

*of the premises wiring electrode.*





-Glenn



*From:* re-wrenches-bounces at lists.re-wrenches.org [
mailto:re-wrenches-bounces at lists.re-wrenches.org<re-wrenches-bounces at lists.re-wrenches.org>]
*On Behalf Of *Jason Szumlanski
*Sent:* Monday, December 09, 2013 2:22 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only



I had to quit watching at noon, so I was disappointed to have missed the
theatrics. I just installed a system on my home to NEC 2008 as is followed
here. I have convinced a local plans reviewer that since it was removed in
NEC 2011, the building official should waive the 690.47(D) requirement for
rooftop systems. He specifically asked me if it would return in NEC 2014,
and if I am reading this right, the answer is definitely "no."



Since there was no aesthetically acceptable way to run the additional GEC
in my case and make it "as close as practicable (which is ambiguous
anyway), I cut it out immediately following inspection - something I would
NEVER recommend a customer do, of course. Nonetheless, I feel this was a
reasonable and acceptable move given that there are thousands of systems
out there inspected under NEC 2011 that have not additional grounding
electrode.



I will continue to listen with great interest...



Jason Szumlanski

Fafco Solar






On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico <
Richard.L.Ratico at valley.net> wrote:


Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to
carefully think through and discuss the issue, in contrast to what was
permitted
on his "show"?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/166553dc/attachment.htm>
Brian Mehalic
2013-12-09 19:30:23 UTC
Permalink
Here's a link to the video:

http://youtu.be/YuDqXFvRv94

Brian
I had to quit watching at noon, so I was disappointed to have missed the theatrics. I just installed a system on my home to NEC 2008 as is followed here. I have convinced a local plans reviewer that since it was removed in NEC 2011, the building official should waive the 690.47(D) requirement for rooftop systems. He specifically asked me if it would return in NEC 2014, and if I am reading this right, the answer is definitely "no."
Since there was no aesthetically acceptable way to run the additional GEC in my case and make it "as close as practicable (which is ambiguous anyway), I cut it out immediately following inspection - something I would NEVER recommend a customer do, of course. Nonetheless, I feel this was a reasonable and acceptable move given that there are thousands of systems out there inspected under NEC 2011 that have not additional grounding electrode.
I will continue to listen with great interest...
Jason Szumlanski
Fafco Solar
Post by Doug Wells
Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better to
carefully think through and discuss the issue, in contrast to what was permitted
on his "show"?
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
www.re-wrenches.org/etiquette.htm
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/dd59fbf8/attachment-0001.htm>
Brian Mehalic
2013-12-09 20:03:49 UTC
Permalink
And it's definitely back in 2014.

Typos courtesy of my iPhone.
I had to quit watching at noon, so I was disappointed to have missed the theatrics. I just installed a system on my home to NEC 2008 as is followed here. I have convinced a local plans reviewer that since it was removed in NEC 2011, the building official should waive the 690.47(D) requirement for rooftop systems. He specifically asked me if it would return in NEC 2014, and if I am reading this right, the answer is definitely "no."
Since there was no aesthetically acceptable way to run the additional GEC in my case and make it "as close as practicable (which is ambiguous anyway), I cut it out immediately following inspection - something I would NEVER recommend a customer do, of course. Nonetheless, I feel this was a reasonable and acceptable move given that there are thousands of systems out there inspected under NEC 2011 that have not additional grounding electrode.
I will continue to listen with great interest...
Jason Szumlanski
Fafco Solar
Post by Doug Wells
Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better to
carefully think through and discuss the issue, in contrast to what was permitted
on his "show"?
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
www.re-wrenches.org/etiquette.htm
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/a43c6854/attachment-0001.htm>
Glenn Burt
2013-12-09 20:50:50 UTC
Permalink
The bad news from the 2014 codebook:



690.47 Grounding Electrode System.

(D) Additional Auxiliary Electrodes for Array Grounding.

A grounding electrode shall be installed in accordance

with 250.52 and 250.54 at the location of all ground- and

pole-mounted PV arrays and as close as practicable to the

location of roof-mounted PV arrays. The electrodes shall be

connected directly to the array frame(s) or structure. The dc

grounding electrode conductor shall be sized according to

250.166. Additional electrodes are not permitted to be used

as a substitute for equipment bonding or equipment grounding

conductor requirements. The structure of a ground- or

pole-mounted PV array shall be permitted to be considered

a grounding electrode if it meets the requirements of

250.52. Roof-mounted PV arrays shall be permitted to use

the metal frame of a building or structure if the requirements

of 250.52(A)(2) are met.

Exception No. 1: An array grounding electrode(s) shall

not be required where the load served by the array is integral

with the array.

Exception No. 2: An additional array grounding electrode(

s) shall not be required if located within 1.8 m (6 ft)

of the premises wiring electrode.





-Glenn



From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Monday, December 09, 2013 2:22 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only



I had to quit watching at noon, so I was disappointed to have missed the
theatrics. I just installed a system on my home to NEC 2008 as is followed
here. I have convinced a local plans reviewer that since it was removed in
NEC 2011, the building official should waive the 690.47(D) requirement for
rooftop systems. He specifically asked me if it would return in NEC 2014,
and if I am reading this right, the answer is definitely "no."



Since there was no aesthetically acceptable way to run the additional GEC in
my case and make it "as close as practicable (which is ambiguous anyway), I
cut it out immediately following inspection - something I would NEVER
recommend a customer do, of course. Nonetheless, I feel this was a
reasonable and acceptable move given that there are thousands of systems out
there inspected under NEC 2011 that have not additional grounding electrode.



I will continue to listen with great interest...



Jason Szumlanski

Fafco Solar





<https://wisestamp.appspot.com/pixview.gif?p=chrome&v=3.21.0&t=1386616464493
&u=ce9344a8140ce271>



On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico
<Richard.L.Ratico at valley.net> wrote:


Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to
carefully think through and discuss the issue, in contrast to what was
permitted
on his "show"?





-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/465a75ba/attachment-0001.htm>
Brian Mehalic
2013-12-09 21:21:26 UTC
Permalink
I agree with Mike on this, as written this is a bad Section, and in reality
there is no need for it, so deleting it is better than trying to fix
something that is unnecessary.

The 2014 690.7(D) language has changed - the title is now "Additional
Auxiliary Electrodes.."; in 2008 the title to be "Additional
Electrodes...". It can be confusing to keep the terminology straight, but:


- "Additional Electrodes" from 2008 is seemingly undefined,
- "Supplemental Electrodes" may be required as part of the grounding
electrode system per 250.53(A)(2) and (3)
- Auxiliary electrodes are defined in 250.54


It's the allowances for Auxiliary Electrodes which cause the problem.
250.54, which must be followed per 690.47(D), states that auxiliary
electrodes do not have to be bonded to the grounded electrode system (as is
typically required of all present electrodes per 250.50), nor does it have
to follow the bonding jumper sizing requirements of 250.53(C).

This creates the problem Mike describes - two connections to ground that
can have dramatically different potential between them in the event of a
lightning incident.

I've always been a proponent of bonding residential pole and ground-mounted
PV structures back to the grounding system of the building they serve.
Large ground-mounted solar farms have lot of
auxiliary/supplemental/additional electrodes in the form of pilings, and
the systems I work on have these all bonded together and back to the
electrodes at the inverter pads - it's extra copper in the ground but it
helps alleviate the problem of different potentials.

The problem is for roof-mounted systems; the 2008 language, by not
explicitly calling it an auxiliary electrode, basically meant that
inspectors were requiring the additional electrode to be bonded to the
existing grounding electrode system on the building - which alleviates the
concerns of having two connections to the Earth. Now 2014 calls it
"Auxiliary" and the language in 250 specifically says it doesn't have to be
bonded to the grounding electrode system - enter the safety concerns
described by Mike and Bill.

Not having to bond the 690.47(D) Auxiliary electrode to the grounding
electrode system alleviates some of the pain of having to put that rod in,
so I imagine that many installers will take this route if the AHJ allows
it. Thus the need to do something about this, before it lingers for years
and years. So...go Bill!





Brian Mehalic
NABCEP Certified Solar PV Installation Professional? R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org
*690.47 Grounding Electrode System.*
*(D) Additional Auxiliary Electrodes for Array Grounding.*
A grounding electrode shall be installed in accordance
with 250.52 and 250.54 at the location of all ground- and
pole-mounted PV arrays and as close as practicable to the
location of roof-mounted PV arrays. The electrodes shall be
connected directly to the array frame(s) or structure. The dc
grounding electrode conductor shall be sized according to
250.166. Additional electrodes are not permitted to be used
as a substitute for equipment bonding or equipment grounding
conductor requirements. The structure of a ground- or
pole-mounted PV array shall be permitted to be considered
a grounding electrode if it meets the requirements of
250.52. Roof-mounted PV arrays shall be permitted to use
the metal frame of a building or structure if the requirements
of 250.52(A)(2) are met.
*Exception No. 1: An array grounding electrode(s) shall*
*not be required where the load served by the array is integral*
*with the array.*
*Exception No. 2: An additional array grounding electrode(*
*s) shall not be required if located within 1.8 m (6 ft)*
*of the premises wiring electrode.*
-Glenn
re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Jason Szumlanski
*Sent:* Monday, December 09, 2013 2:22 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only
I had to quit watching at noon, so I was disappointed to have missed the
theatrics. I just installed a system on my home to NEC 2008 as is followed
here. I have convinced a local plans reviewer that since it was removed in
NEC 2011, the building official should waive the 690.47(D) requirement for
rooftop systems. He specifically asked me if it would return in NEC 2014,
and if I am reading this right, the answer is definitely "no."
Since there was no aesthetically acceptable way to run the additional GEC
in my case and make it "as close as practicable (which is ambiguous
anyway), I cut it out immediately following inspection - something I would
NEVER recommend a customer do, of course. Nonetheless, I feel this was a
reasonable and acceptable move given that there are thousands of systems
out there inspected under NEC 2011 that have not additional grounding
electrode.
I will continue to listen with great interest...
Jason Szumlanski
Fafco Solar
On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico <
Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to
carefully think through and discuss the issue, in contrast to what was
permitted
on his "show"?
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
www.re-wrenches.org/etiquette.htm
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/d298697b/attachment-0001.htm>
August Goers
2013-12-09 21:47:58 UTC
Permalink
Hi Glenn,



This is a confusing passage without seeing the context from the other parts
of 690.47 (A, B, C etc). Can you send the full passage if it?s handy for
you? My 2014 NEC is in the mail so I have yet to see the full implications
of this section.



Best,



August



*From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Glenn Burt
*Sent:* Monday, December 09, 2013 12:51 PM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only



The bad news from the 2014 codebook:



*690.47 Grounding Electrode System.*

*(D) Additional Auxiliary Electrodes for Array Grounding.*

A grounding electrode shall be installed in accordance

with 250.52 and 250.54 at the location of all ground- and

pole-mounted PV arrays and as close as practicable to the

location of roof-mounted PV arrays. The electrodes shall be

connected directly to the array frame(s) or structure. The dc

grounding electrode conductor shall be sized according to

250.166. Additional electrodes are not permitted to be used

as a substitute for equipment bonding or equipment grounding

conductor requirements. The structure of a ground- or

pole-mounted PV array shall be permitted to be considered

a grounding electrode if it meets the requirements of

250.52. Roof-mounted PV arrays shall be permitted to use

the metal frame of a building or structure if the requirements

of 250.52(A)(2) are met.

*Exception No. 1: An array grounding electrode(s) shall*

*not be required where the load served by the array is integral*

*with the array.*

*Exception No. 2: An additional array grounding electrode(*

*s) shall not be required if located within 1.8 m (6 ft)*

*of the premises wiring electrode.*





-Glenn



*From:* re-wrenches-bounces at lists.re-wrenches.org [
mailto:re-wrenches-bounces at lists.re-wrenches.org<re-wrenches-bounces at lists.re-wrenches.org>]
*On Behalf Of *Jason Szumlanski
*Sent:* Monday, December 09, 2013 2:22 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only



I had to quit watching at noon, so I was disappointed to have missed the
theatrics. I just installed a system on my home to NEC 2008 as is followed
here. I have convinced a local plans reviewer that since it was removed in
NEC 2011, the building official should waive the 690.47(D) requirement for
rooftop systems. He specifically asked me if it would return in NEC 2014,
and if I am reading this right, the answer is definitely "no."



Since there was no aesthetically acceptable way to run the additional GEC
in my case and make it "as close as practicable (which is ambiguous
anyway), I cut it out immediately following inspection - something I would
NEVER recommend a customer do, of course. Nonetheless, I feel this was a
reasonable and acceptable move given that there are thousands of systems
out there inspected under NEC 2011 that have not additional grounding
electrode.



I will continue to listen with great interest...



Jason Szumlanski

Fafco Solar






On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico <
Richard.L.Ratico at valley.net> wrote:


Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to
carefully think through and discuss the issue, in contrast to what was
permitted
on his "show"?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/166553dc/attachment-0001.htm>
Bill Brooks
2013-12-09 21:14:04 UTC
Permalink
Dick,

It sounds like you are not a big Mike Holt fan. There is no requirement for
that. The language in the 2008 NEC was poor, at best. It was a complete mess
up of a proposal that John Wiles and I was involved with--sounds like you
were involved as well. A member of the CMP13 took the proposal and
essentially destroyed it.

The original proposal was to require an electrode on ground-mounted
structure. The roof-mounted requirement was a complete mistake--and
potentially dangerous in most cases.

My approach is to work with another member of our CMP4 panel to write an
article for the IAEI News and explain what was intended. Since the language
is very ambiguous, that can work in the favor of providing an opinion that
is a safe version of 690.47(D).

Bottom line is that any building that already has a grounding electrode
should not have an additional electrode added.

Bill.


-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Richard L
Ratico
Sent: Monday, December 09, 2013 6:22 AM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only

I watched most of the streaming video of Mike Holt and six PV industry
professionals this weekend. The most interesting aspect of it was Mr. Holt's
very dramatic build up to the Sunday discussion of Article 690.47(D) which
brings back the requirement for an auxiliary grounding electrode for PV
arrays.
He used everything short of drum rolls to build anticipation for this part
of the presentation.

Having personally contributed a short piece on this subject for SolarPro
magazine along with Bill Brooks and John Wiles in 2008, I looked forward to
this discussion. Finally, midday Sunday, instead of a discussion of an
important and controversial part of the 2014 code, we received a rant by Mr.
Holt demanding an immediate and unprecedented withdrawal of the article.

Prior to his remarks, in contrast to the preceding article discussions, Mr.
Holt asked that the guest panel not make any comments that would explain how
the requirement came to return to the code after being eliminated in the
2011 edition, or any comment that might "confuse" the issue. To my very
great surprise and disappointment, they complied, uttering not a single
word, nodding their heads and moving on to the next article.

After all the buildup by Mr. Holt, the "discussion" amounted to his monolog,
which if parsed, though stated to be for safety concerns, seemed primarily
an exercise designed to sell his books, videos and consulting services on
grounding. This was of course expected. The weekend live streaming was
generously offered free of charge, a rare opportunity to hear current PV
expert opinion on the NEC. My concern is that Mr. Holt's control of the
process here inhibited the dialog that should have taken place.

There are significant implications of allowing his opinion to go
unchallenged.
Is there, or is there not, any merit in 690.47(D)? Could the language be
better?
Could the requirement be modified to make it better rather than simply
discarding it? Does accepting his argument mean all those systems installed
according to the 2008 code are unsafe?

Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to carefully think through and discuss the issue, in contrast to what was
permitted on his "show"?

Dick Ratico
Solarwind Electric


--- You wrote:
Dear Wrenches,

Several of your co-wrenches are helping Mike Holt with the video companion
to his PV & the NEC 2014 book. So since you spend all your weekdays thinking
about the NEC, what better way to spend this weekend than to watch NEC nerds
discuss the meanings of shalls and shall-nots, the unwelcome return of
690.47(D), and the continued flights of our favorite sections to 705, right?
Before you answer that, know that you can also ask questions during the
video in case something is unclear or if we're wrong about something.

Broadcasting (free) from:
www.MikeHolt.com/live

Times:
~9a-4p ET Sat 12/7
~9a-5p ET Sun 12/8

Video from this weekend will be what's edited into the official DVD that
Mike puts out in the next few weeks.

Because Bill Brooks has a great joke about separate direct-current grounding
electrode systems bonded to the alternating current grounding electrode
systems that you don't want to miss, Dave

PS If this post violates list etiquette, my apologies in advance, Michael.
We don't get a commission, if that helps...
_______________________________________
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com
Doug Wells
2013-12-09 16:30:48 UTC
Permalink
Richard,

I agree. I caught part of the streaming as well.
Thanks for sharing.
Bringing lightning protection into the discussion is a whole other can of worms.
He made a variety of assumptions.
1. That the auxiliary rods were not bonded. For instance, I was trained in the exact opposite manner for ground mounts and off grid. Installing a rod at each pole mount, inverter and generator. But then bonding all of these rods together, with the intention of keeping all metal, modules, etc in the entire system at the same potential. This approach seems to really be echoing his own comments of keeping everything underground bonded. The important part seems to be having the DC electrical bonding, GFI etc and the AC neutral bond in only one location.
2. Ground lightning strikes will create differences in potential on all conductors. The insulation on most conductors buried in conduit is only good to 600 to 1000 volts at best. If there is a strike creating 100,000's of volts then all conductors will surely see current and voltage spikes. This is why we always install Surge Arrestors.
3. While I can appreciate the physics of lightning protection, I have it on my house, I am not so sure about its impact on a large PV array. I have a hard time accepting that a 1-2 foot spike of metal on the roof connected directly to ground will handle anything near a direct strike like he showed in the picture. Unfortunately, in that regard you get hit, or you don't. In fact, some lightning folks will admit that lightning protection can encourage the passage of some strikes. But the question here seems to be ---1. Is 1000 ft2 of aluminum rectangles, racking and wire, less conductive than a 2 foot metal spike. And is the extra 20-100 feet that the grounds pass to the rod, really enough to resist current in a strike. 2. If logic holds that a lightning protection system has merit, then wouldn't bringing every rail to ground at multiple points and then bonding them all together do the same thing.
I am not saying that this is the way it should be done, but making the point that it is essentially the same thing.
So, I respect Mike and what he is trying to do for many people, which is provide clear and accurate training materials.
However, I agree with Richard that I would like to hear from all the voices in the industry that have their minds around this as well.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

On Dec 9, 2013, at 9:21 AM, Richard L Ratico wrote:

I watched most of the streaming video of Mike Holt and six PV industry
professionals this weekend. The most interesting aspect of it was Mr. Holt's
very dramatic build up to the Sunday discussion of Article 690.47(D) which
brings back the requirement for an auxiliary grounding electrode for PV arrays.
He used everything short of drum rolls to build anticipation for this part of
the presentation.

Having personally contributed a short piece on this subject for SolarPro
magazine along with Bill Brooks and John Wiles in 2008, I looked forward to this
discussion. Finally, midday Sunday, instead of a discussion of an important and
controversial part of the 2014 code, we received a rant by Mr. Holt demanding an
immediate and unprecedented withdrawal of the article.

Prior to his remarks, in contrast to the preceding article discussions, Mr. Holt
asked that the guest panel not make any comments that would explain how the
requirement came to return to the code after being eliminated in the 2011
edition, or any comment that might "confuse" the issue. To my very great
surprise and disappointment, they complied, uttering not a single word, nodding
their heads and moving on to the next article.

After all the buildup by Mr. Holt, the "discussion" amounted to his monolog,
which if parsed, though stated to be for safety concerns, seemed primarily an
exercise designed to sell his books, videos and consulting services on
grounding. This was of course expected. The weekend live streaming was
generously offered free of charge, a rare opportunity to hear current PV expert
opinion on the NEC. My concern is that Mr. Holt's control of the process here
inhibited the dialog that should have taken place.

There are significant implications of allowing his opinion to go unchallenged.
Is there, or is there not, any merit in 690.47(D)? Could the language be better?
Could the requirement be modified to make it better rather than simply
discarding it? Does accepting his argument mean all those systems installed
according to the 2008 code are unsafe?

Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better to
carefully think through and discuss the issue, in contrast to what was permitted
on his "show"?

Dick Ratico
Solarwind Electric


--- You wrote:
Dear Wrenches,

Several of your co-wrenches are helping Mike Holt with the video
companion to his PV & the NEC 2014 book. So since you spend all your
weekdays thinking about the NEC, what better way to spend this weekend
than to watch NEC nerds discuss the meanings of shalls and shall-nots,
the unwelcome return of 690.47(D), and the continued flights of our
favorite sections to 705, right? Before you answer that, know that you
can also ask questions during the video in case something is unclear or
if we're wrong about something.

Broadcasting (free) from:
www.MikeHolt.com/live

Times:
~9a-4p ET Sat 12/7
~9a-5p ET Sun 12/8

Video from this weekend will be what's edited into the official DVD that
Mike puts out in the next few weeks.

Because Bill Brooks has a great joke about separate direct-current
grounding electrode systems bonded to the alternating current grounding
electrode systems that you don't want to miss,
Dave

PS If this post violates list etiquette, my apologies in advance,
Michael. We don't get a commission, if that helps...
_______________________________________
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
Jason Szumlanski
2013-12-09 19:21:40 UTC
Permalink
I had to quit watching at noon, so I was disappointed to have missed the
theatrics. I just installed a system on my home to NEC 2008 as is followed
here. I have convinced a local plans reviewer that since it was removed in
NEC 2011, the building official should waive the 690.47(D) requirement for
rooftop systems. He specifically asked me if it would return in NEC 2014,
and if I am reading this right, the answer is definitely "no."

Since there was no aesthetically acceptable way to run the additional GEC
in my case and make it "as close as practicable (which is ambiguous
anyway), I cut it out immediately following inspection - something I would
NEVER recommend a customer do, of course. Nonetheless, I feel this was a
reasonable and acceptable move given that there are thousands of systems
out there inspected under NEC 2011 that have not additional grounding
electrode.

I will continue to listen with great interest...

Jason Szumlanski

Fafco Solar





On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico <
Post by Doug Wells
Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to
carefully think through and discuss the issue, in contrast to what was
permitted
on his "show"?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/8a384d4d/attachment-0001.htm>
Bill Brooks
2013-12-09 21:14:04 UTC
Permalink
Dick,

It sounds like you are not a big Mike Holt fan. There is no requirement for
that. The language in the 2008 NEC was poor, at best. It was a complete mess
up of a proposal that John Wiles and I was involved with--sounds like you
were involved as well. A member of the CMP13 took the proposal and
essentially destroyed it.

The original proposal was to require an electrode on ground-mounted
structure. The roof-mounted requirement was a complete mistake--and
potentially dangerous in most cases.

My approach is to work with another member of our CMP4 panel to write an
article for the IAEI News and explain what was intended. Since the language
is very ambiguous, that can work in the favor of providing an opinion that
is a safe version of 690.47(D).

Bottom line is that any building that already has a grounding electrode
should not have an additional electrode added.

Bill.


-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Richard L
Ratico
Sent: Monday, December 09, 2013 6:22 AM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town,
limited time only

I watched most of the streaming video of Mike Holt and six PV industry
professionals this weekend. The most interesting aspect of it was Mr. Holt's
very dramatic build up to the Sunday discussion of Article 690.47(D) which
brings back the requirement for an auxiliary grounding electrode for PV
arrays.
He used everything short of drum rolls to build anticipation for this part
of the presentation.

Having personally contributed a short piece on this subject for SolarPro
magazine along with Bill Brooks and John Wiles in 2008, I looked forward to
this discussion. Finally, midday Sunday, instead of a discussion of an
important and controversial part of the 2014 code, we received a rant by Mr.
Holt demanding an immediate and unprecedented withdrawal of the article.

Prior to his remarks, in contrast to the preceding article discussions, Mr.
Holt asked that the guest panel not make any comments that would explain how
the requirement came to return to the code after being eliminated in the
2011 edition, or any comment that might "confuse" the issue. To my very
great surprise and disappointment, they complied, uttering not a single
word, nodding their heads and moving on to the next article.

After all the buildup by Mr. Holt, the "discussion" amounted to his monolog,
which if parsed, though stated to be for safety concerns, seemed primarily
an exercise designed to sell his books, videos and consulting services on
grounding. This was of course expected. The weekend live streaming was
generously offered free of charge, a rare opportunity to hear current PV
expert opinion on the NEC. My concern is that Mr. Holt's control of the
process here inhibited the dialog that should have taken place.

There are significant implications of allowing his opinion to go
unchallenged.
Is there, or is there not, any merit in 690.47(D)? Could the language be
better?
Could the requirement be modified to make it better rather than simply
discarding it? Does accepting his argument mean all those systems installed
according to the 2008 code are unsafe?

Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would it not be better
to carefully think through and discuss the issue, in contrast to what was
permitted on his "show"?

Dick Ratico
Solarwind Electric


--- You wrote:
Dear Wrenches,

Several of your co-wrenches are helping Mike Holt with the video companion
to his PV & the NEC 2014 book. So since you spend all your weekdays thinking
about the NEC, what better way to spend this weekend than to watch NEC nerds
discuss the meanings of shalls and shall-nots, the unwelcome return of
690.47(D), and the continued flights of our favorite sections to 705, right?
Before you answer that, know that you can also ask questions during the
video in case something is unclear or if we're wrong about something.

Broadcasting (free) from:
www.MikeHolt.com/live

Times:
~9a-4p ET Sat 12/7
~9a-5p ET Sun 12/8

Video from this weekend will be what's edited into the official DVD that
Mike puts out in the next few weeks.

Because Bill Brooks has a great joke about separate direct-current grounding
electrode systems bonded to the alternating current grounding electrode
systems that you don't want to miss, Dave

PS If this post violates list etiquette, my apologies in advance, Michael.
We don't get a commission, if that helps...
_______________________________________
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com
Richard L Ratico
2013-12-10 07:07:12 UTC
Permalink
An embedded and charset-unspecified text was scrubbed...
Name: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131210/b5a4edaa/attachment.asc>
Christopher Warfel
2013-12-10 17:46:30 UTC
Permalink
Really good on those nights when Curling is not on
ESPN......................
Post by Dave Click
Dear Wrenches,
Several of your co-wrenches are helping Mike Holt with the video
companion to his PV & the NEC 2014 book. So since you spend all your
weekdays thinking about the NEC, what better way to spend this weekend
than to watch NEC nerds discuss the meanings of shalls and shall-nots,
the unwelcome return of 690.47(D), and the continued flights of our
favorite sections to 705, right? Before you answer that, know that you
can also ask questions during the video in case something is unclear
or if we're wrong about something.
www.MikeHolt.com/live
~9a-4p ET Sat 12/7
~9a-5p ET Sun 12/8
Video from this weekend will be what's edited into the official DVD
that Mike puts out in the next few weeks.
Because Bill Brooks has a great joke about separate direct-current
grounding electrode systems bonded to the alternating current
grounding electrode systems that you don't want to miss,
Dave
PS If this post violates list etiquette, my apologies in advance,
Michael. We don't get a commission, if that helps...
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
www.re-wrenches.org/etiquette.htm
www.members.re-wrenches.org
--
Christopher Warfel, P.E.
ENTECH Engineering, Inc.
Energy Utilization Experts
(401)466-8978

The information contained within this communication shall
be considered confidential and shall not be retransmitted
without knowledge of the sender. Please contact us if
this email reached you in error. Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131210/db4e1b38/attachment.htm>
Dave Click
2013-12-07 01:25:27 UTC
Permalink
Dear Wrenches,

Several of your co-wrenches are helping Mike Holt with the video
companion to his PV & the NEC 2014 book. So since you spend all your
weekdays thinking about the NEC, what better way to spend this weekend
than to watch NEC nerds discuss the meanings of shalls and shall-nots,
the unwelcome return of 690.47(D), and the continued flights of our
favorite sections to 705, right? Before you answer that, know that you
can also ask questions during the video in case something is unclear or
if we're wrong about something.

Broadcasting (free) from:
www.MikeHolt.com/live

Times:
~9a-4p ET Sat 12/7
~9a-5p ET Sun 12/8

Video from this weekend will be what's edited into the official DVD that
Mike puts out in the next few weeks.

Because Bill Brooks has a great joke about separate direct-current
grounding electrode systems bonded to the alternating current grounding
electrode systems that you don't want to miss,
Dave

PS If this post violates list etiquette, my apologies in advance,
Michael. We don't get a commission, if that helps...
Richard L Ratico
2013-12-09 14:21:35 UTC
Permalink
An embedded and charset-unspecified text was scrubbed...
Name: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131209/f9aa00df/attachment-0001.txt>
Richard L Ratico
2013-12-10 07:07:12 UTC
Permalink
An embedded and charset-unspecified text was scrubbed...
Name: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131210/b5a4edaa/attachment-0001.asc>
Christopher Warfel
2013-12-10 17:46:30 UTC
Permalink
Really good on those nights when Curling is not on
ESPN......................
Post by Dave Click
Dear Wrenches,
Several of your co-wrenches are helping Mike Holt with the video
companion to his PV & the NEC 2014 book. So since you spend all your
weekdays thinking about the NEC, what better way to spend this weekend
than to watch NEC nerds discuss the meanings of shalls and shall-nots,
the unwelcome return of 690.47(D), and the continued flights of our
favorite sections to 705, right? Before you answer that, know that you
can also ask questions during the video in case something is unclear
or if we're wrong about something.
www.MikeHolt.com/live
~9a-4p ET Sat 12/7
~9a-5p ET Sun 12/8
Video from this weekend will be what's edited into the official DVD
that Mike puts out in the next few weeks.
Because Bill Brooks has a great joke about separate direct-current
grounding electrode systems bonded to the alternating current
grounding electrode systems that you don't want to miss,
Dave
PS If this post violates list etiquette, my apologies in advance,
Michael. We don't get a commission, if that helps...
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
www.re-wrenches.org/etiquette.htm
www.members.re-wrenches.org
--
Christopher Warfel, P.E.
ENTECH Engineering, Inc.
Energy Utilization Experts
(401)466-8978

The information contained within this communication shall
be considered confidential and shall not be retransmitted
without knowledge of the sender. Please contact us if
this email reached you in error. Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131210/db4e1b38/attachment-0001.htm>
Loading...